Larkin LCA662AB motor failure after freeze-over

Home Threads Equipment Larkin LCA662AB motor failure after freeze-over

Viewing 1 reply thread
  • Author
    Posts
    • #2591
      Ben Cheek
      Keymaster

      The Larkin LCA662AB Walk-in Cooler Unit froze over after the door to the walk-in was left open allowing warm moist air to enter and condense on the unit. According to Rick Weaver, the ice had reached and immobilized the fan. After thawing, the fan would turn slowly and the motor generated excess heat.

      A new motor was purchase from Meier Supply (see equpiment page) and installed. This motor is an updated HeatCraft 25309501S model that replaces the original equipment. One note: the fan has a two-pin connector that plugs into a socket attached to the wall of the fan chamber. No need to remove side panels.

      • This topic was modified 1 month, 1 week ago by Ben Cheek.
    • #2614
      Ben Cheek
      Keymaster

      Conversation with the techs (Rick and Joey) from Blueline Mechanical indicated that the charge was low on the Walk-in Cooler system, possibly leading to icing and destroying the fan.